Richard Haselgrove ![]() Send message Joined: 4 Jul 99 Posts: 14690 Credit: 200,643,578 RAC: 874
|
Actually, that's a misnomer. It takes 0.1 amps to stop your heart... I think the point that I was trying to make was that for any given contact impedance (wet or dry, area of contact etc.) the higher voltage - within the domestic or industrial range - will drive a higher current: and as you say, it's the current which kills. At very much higher voltages, one is usually saved by the inability of the source to provide any appreciable current - which is why schoolroom fun and games with Van de Graaff generators are permitted. |
|
Kevin Olley Send message Joined: 3 Aug 99 Posts: 906 Credit: 261,085,289 RAC: 572
|
Sorry was refuring to 110v used on UK construction sites, 110v between live - return but only 55v to earth. Kevin
|
|
justsomeguy Send message Joined: 27 May 99 Posts: 84 Credit: 6,084,595 RAC: 11
|
Nope, they are permitted 'cause some of them kids just need to be juiced! :) "Two things are infinite: The universe and human stupidity; and I'm not sure about the universe." - Albert Einstein
|
Donald L. Johnson Send message Joined: 5 Aug 02 Posts: 8240 Credit: 14,654,533 RAC: 20
|
As someone else above noted, there is less loss in the higher voltage. I know with water Yes, line losses are proportional to the square of the current (IIR) Donald Infernal Optimist / Submariner, retired |
HAL9000 Send message Joined: 11 Sep 99 Posts: 6534 Credit: 196,805,888 RAC: 57
|
Out of curiosity. Might that get done as far back as in the meter? In every panel I have opened, in OK & NJ, the neutral & ground bus bars haven't been connected. Also I normally see a small voltage potential between neutral & earth ground at the outlets. Normally <1v but I have seen as high as 3v between the two. SETI@home classic workunits: 93,865 CPU time: 863,447 hours Join the [url=http://tinyurl.com/8y46zvu]BP6/VP6 User Group[
|
SciManStev ![]() Send message Joined: 20 Jun 99 Posts: 6666 Credit: 121,090,076 RAC: 0
|
Also I normally see a small voltage potential between neutral & earth ground at the outlets. Normally <1v but I have seen as high as 3v between the two. This is due to the resistance between the ground and return. Any current caught in a ground loop, passes over that resistance, and causes a voltage. V=IR or Voltage = Current times Resistance. Where Voltage is in Volts (AC or DC), current in in Amps, and resistance is in Ohms. Power (Watts) = Current (Amps) times voltage (Volts) These equations can not be violated for any reason. If a circuit draws 100 watts, and the voltage drops, then it will draw more current to make up for it. This continues until the supply circuit can no longer handle it, and then total wattage decreases. Steve Warning, addicted to SETI crunching! Crunching as a member of GPU Users Group. GPUUG Website |
razamatraz Send message Joined: 23 Oct 07 Posts: 142 Credit: 27,815,748 RAC: 0
|
Most good power supplies are actually more efficient at the higher voltage. A lot of the 80+ Golds just barely make gold on 110V but surpass it on 220V. |
Raistmer Send message Joined: 16 Jun 01 Posts: 6325 Credit: 106,370,077 RAC: 121
|
Most good power supplies are actually more efficient at the higher voltage. A lot of the 80+ Golds just barely make gold on 110V but surpass it on 220V. +1. There are always loss due to heat and if one recall scool, Q=I*I*R*t. Power P=IU, so, if one transfer same power on higher voltage one will have lower current and lower Joule's heat generation. That's why long-range electricity transfers are always on very high voltages. |
Gary Charpentier ![]() Send message Joined: 25 Dec 00 Posts: 31649 Credit: 53,134,872 RAC: 32
|
Also I normally see a small voltage potential between neutral & earth ground at the outlets. Normally <1v but I have seen as high as 3v between the two. Actually due to resistance in the neutral circuit. It is the one carrying the current. The ground circuit just carries the power to move the meter. I might begin to worry at 3V if the conductor size was correct for the current being carried. Check your electric code. I've seen some wild things here because the utility here uses a single cable, the two insulated hots wrapped around a bare neutral. The bare neutral is AL wrapped over a steel core. Squirrels like to sharpen their teeth on the AL and frequently break the connection. Then the steel has to carry the current and it isn't up to the task. Blinking lights all over the neighborhood.
|
HAL9000 Send message Joined: 11 Sep 99 Posts: 6534 Credit: 196,805,888 RAC: 57
|
Also I normally see a small voltage potential between neutral & earth ground at the outlets. Normally <1v but I have seen as high as 3v between the two. The supply line going into my dads place was like that before he upgraded to 150A service. Which also resulted in it being a buried line. I haven't seen anything over 1V in a while. Since I just got home from work I did some checking in my new place and I got between 80-90mV depending on the outlets location. It has been a few years since I finished my degree for electrical engineering, but I don't recall us doing to much with the NEC. Doing some checking NJ doesn't seem to have adopted the 2011 version yet. SETI@home classic workunits: 93,865 CPU time: 863,447 hours Join the [url=http://tinyurl.com/8y46zvu]BP6/VP6 User Group[
|
|
Cosmic_Ocean Send message Joined: 23 Dec 00 Posts: 3027 Credit: 13,516,867 RAC: 13
|
Not supposed to be three...should be four conductors...hot, hot, neutral Technically, yes, that is how it is supposed to be, but there are certain applications where it is required by the device. It is not always needed though. I know ranges (cooktop and oven in one unit) have hot-hot-neutral-ground, but clothes dryers have hot-hot-ground (newer, more modern ones have gone to 4-wire). Depends on the device for what kind of setup it is going to have. Hooking a computer power supply up for example, only has three conductors, so you can't have a neutral in there on 240VAC. Uhh... It depends on the local code inspector and regulations for where you are. Around where I live, ground and neutral are bonded in the panel, but other municipalities require that they are separate even through the meter box. The power company ties the two together on the pole, so it still does the same thing anyway. Linux laptop: record uptime: 1511d 20h 19m (ended due to the power brick giving-up) |