Seti@Home UPS Problems - possible solution
Message board moderation
Author | Message |
---|---|
Monty Wild Send message Joined: 10 Mar 00 Posts: 10 Credit: 586,449 RAC: 0 |
This post is more of a solution looking for a problem... I noticed in the technical news that there was trouble with the data cables for the UPSs. If these are APC Smart-UPS UPSs, as the technical news seemed to suggest, I may have a solution to the problem, having had the same problem myself. When one type of data cable is used with these UPSs - i.e.: USB or serial - the UPS will no longer respond via the other type of cable until the UPS is reset. This may be achieved as per instructions I received from APC support: 1) Turn the UPS OFF. 2) Disconnect the USB / Serial cable. 3) Disconnect the mains power cable. 4) Hold the test button down for 5 seconds. You should hear a click. At this point, either type of cable should be useable until one type has been used. I hope this helps and is relevant. |